Help VMC TRIAC
- Hardware/Software: .....
4 Quatros
3 Oracs
2 Easiturn atc
12 station lathe atc
Mach 3 - Location: Quatroland
Re: Help VMC TRIAC
estop button?
- CNC Apprentice
- Hardware/Software: VMC TRIAC with ATC
Re: Help VMC TRIAC
Button ok.
Re: Help VMC TRIAC
Are the drives powered up.
See if you can turn the X axis leadscrew or if the motor is holding it.
- CNC Apprentice
Re: Help VMC TRIAC
I' ll try tomorrow. I don' t understand ... before BALDOR card should fail everything was ok.
- CNC Apprentice
Re: Help VMC TRIAC
I can turn on the coolant.
I can turn the spindle.
But I can not do the homming.
- CNC Apprentice
Re: Help VMC TRIAC
When I try homing, I can turn the X axis leadscrew the motor isn't holding it.
What I do?
What I do?
4 Quatros
3 Oracs
2 Easiturn atc
Re: Help VMC TRIAC
check the supply to the drive psu, probably fuse 4.
- CNC Apprentice
Re: Help VMC TRIAC
I had already checked, it's ok.
Help please!!!!!
Help please!!!!!
Re: Help VMC TRIAC
Are the drives powering up ? Any LED's lighting up on them - you will find the manuals for those here on the forum:
Parker I think: viewtopic.php?t=561
It may be that when the Eurocard failed, it caused a failure on the rack - maybe also the drives as they share the same backplane.
Check around for burnt tracks/fuses on the rack system.
4 Quatros
3 Oracs
2 Easiturn atc
Re: Help VMC TRIAC
on that model, does the second board next to the baldor board supply dc to the control logic, or enable the drives somehow.?
Re: Help VMC TRIAC
AFAIK the 2nd daughter board is just additional IO and the isolated spindle analogue
I don't remember seeing or scanning any information on that card
- CNC Apprentice
Re: Help VMC TRIAC
Eurocard failed probably because I replaced the battery with a wrong.
Before everything was ok just could not remember the tool.
Fuses on the axis cards are ok.
4 Quatros
3 Oracs
2 Easiturn atc
Re: Help VMC TRIAC
is there 24v on the drives
Re: Help VMC TRIAC
If the drives aren't been energised then you need to trace that fault from the diagrams and the manuals.
eg:
viewtopic.php?f=54&t=3068
viewtopic.php?f=54&t=2264
Is the enable signal changing when you release estop - I'm not sure what will exactly happen but power should be applied to the axes drives...
eg:
- CNC Apprentice
Re: Help VMC TRIAC
the 24volts DC is present on the backplane. wires 60 & 61.
I checked the 3 x 20mm fuses on the backplane and are ok
4 Quatros
3 Oracs
2 Easiturn atc
Re: Help VMC TRIAC
make sure the drives are fully pushed into the sockets.
- CNC Apprentice
Re: Help VMC TRIAC
When i try homing the X axis baldor card writes "H"
When i try homing the Y axis baldor card writes "8"
When i try homing the Z axis baldor card writes "8"
I checked DC on terminals shown on the picture: is not present.
I checked all fuses in the axis card and in backplane: are ok.
- ASSI.jpg (17.63 KiB) Viewed 39820 times
Re: Help VMC TRIAC
It may be worth checking that the ribbon cable between the custon card & motion control card is fully seated.
- CNC Apprentice
Re: Help VMC TRIAC
YESSSSSS!!!! I did it!
The machine works!
The fault has been an abnormal contact of a fuse on the backplane!
Thank you all for your advice and thanks to Denford for the support.
The machine works!
Re: Help VMC TRIAC
Fantastico
