Help VMC TRIAC
angel-tech
Hardware/Software: .....
4 Quatros
3 Oracs
2 Easiturn atc
12 station lathe atc
Mach 3
Re: Help VMC TRIAC
Post by angel-tech » Fri 23 Mar , 2012 21:30 pm
estop button?
ilbiondo
Hardware/Software: VMC TRIAC with ATC
Re: Help VMC TRIAC
Post by ilbiondo » Sat 24 Mar , 2012 19:25 pm
Button ok.
Re: Help VMC TRIAC
Post by Martin » Sat 24 Mar , 2012 22:28 pm
Are the drives powered up.
See if you can turn the X axis leadscrew or if the motor is holding it.
ilbiondo
Re: Help VMC TRIAC
Post by ilbiondo » Sun 25 Mar , 2012 12:43 pm
I' ll try tomorrow. I don' t understand ... before BALDOR card should fail everything was ok. :cry:
ilbiondo
Re: Help VMC TRIAC
Post by ilbiondo » Mon 26 Mar , 2012 8:21 am
I can turn on the coolant.
I can turn the spindle.
But I can not do the homming. :?: :?: :?:
ilbiondo
Re: Help VMC TRIAC
Post by ilbiondo » Mon 26 Mar , 2012 11:43 am
When I try homing, I can turn the X axis leadscrew the motor isn't holding it.
What I do?
angel-tech
4 Quatros
3 Oracs
2 Easiturn atc
Mach 3
Re: Help VMC TRIAC
Post by angel-tech » Mon 26 Mar , 2012 13:23 pm
check the supply to the drive psu, probably fuse 4.
ilbiondo
Re: Help VMC TRIAC
Post by ilbiondo » Mon 26 Mar , 2012 13:51 pm
I had already checked, it's ok.
Help please!!!!!
Re: Help VMC TRIAC
Post by Denford Admin » Mon 26 Mar , 2012 14:01 pm
Are the drives powering up ? Any LED's lighting up on them - you will find the manuals for those here on the forum:
Parker I think: viewtopic.php?t=561
It may be that when the Eurocard failed, it caused a failure on the rack - maybe also the drives as they share the same backplane.
Check around for burnt tracks/fuses on the rack system.
angel-tech
4 Quatros
3 Oracs
2 Easiturn atc
Mach 3
Re: Help VMC TRIAC
Post by angel-tech » Mon 26 Mar , 2012 14:33 pm
on that model, does the second board next to the baldor board supply dc to the control logic, or enable the drives somehow.?
Re: Help VMC TRIAC
Post by Denford Admin » Mon 26 Mar , 2012 14:38 pm
AFAIK the 2nd daughter board is just additional IO and the isolated spindle analogue
I don't remember seeing or scanning any information on that card :?
ilbiondo
Re: Help VMC TRIAC
Post by ilbiondo » Mon 26 Mar , 2012 14:39 pm
Eurocard failed probably because I replaced the battery with a wrong. :oops:
Before everything was ok just could not remember the tool.
Fuses on the axis cards are ok.
angel-tech
4 Quatros
3 Oracs
2 Easiturn atc
Mach 3
Re: Help VMC TRIAC
Post by angel-tech » Mon 26 Mar , 2012 14:49 pm
is there 24v on the drives
Re: Help VMC TRIAC
Post by Denford Admin » Mon 26 Mar , 2012 14:52 pm
If the drives aren't been energised then you need to trace that fault from the diagrams and the manuals.
eg:
viewtopic.php?f=54&t=3068
viewtopic.php?f=54&t=2264
Is the enable signal changing when you release estop - I'm not sure what will exactly happen but power should be applied to the axes drives...
ilbiondo
Re: Help VMC TRIAC
Post by ilbiondo » Mon 26 Mar , 2012 15:03 pm
the 24volts DC is present on the backplane. wires 60 & 61.
I checked the 3 x 20mm fuses on the backplane and are ok
angel-tech
4 Quatros
3 Oracs
2 Easiturn atc
Mach 3
Re: Help VMC TRIAC
Post by angel-tech » Mon 26 Mar , 2012 16:01 pm
make sure the drives are fully pushed into the sockets.
ilbiondo
Re: Help VMC TRIAC
Post by ilbiondo » Wed 28 Mar , 2012 8:00 am
When i try homing the X axis baldor card writes "H"
When i try homing the Y axis baldor card writes "8"
When i try homing the Z axis baldor card writes "8"
I checked DC on terminals shown on the picture: is not present.
I checked all fuses in the axis card and in backplane: are ok.
Re: Help VMC TRIAC
Post by Martin » Wed 28 Mar , 2012 8:44 am
It may be worth checking that the ribbon cable between the custon card & motion control card is fully seated.
ilbiondo
Re: Help VMC TRIAC
Post by ilbiondo » Tue 10 Apr , 2012 16:43 pm
YESSSSSS!!!! I did it! :fireworks: :lolol:
The machine works!
The fault has been an abnormal contact of a fuse on the backplane!
Thank you all for your advice and thanks to Denford for the support.
Re: Help VMC TRIAC
Post by Denford Admin » Wed 11 Apr , 2012 14:50 pm
Fantastico :lolol: