Denford CIM-Mitsubishi RV-2AJ Robot Problem

Posted: Tue 14 Jun , 2011 19:56 pm
by ar89
Hi,

I am using Denford CIM. Whenever i try to run a cell of the CIM, including lathe machine and mitsubishi robot; the robot after executing the program does not release interlock.

I think there is a command for releasing robot interlock i.e. OB+4 (at program start) and OB-4 (at program end). But whenever i run the program having these commands the robot gives an error "L.0091".
Please help me to get rid of this problem.

Re: Denford CIM-Mitsubishi RV-2AJ Robot Problem

Posted: Thu 16 Jun , 2011 15:46 pm
by bradders
Error Message :- L0091

From the Mitsubishi Error list manual

Error Message :- This signal is already assigned to the dedicated output
Cause :- This signal cannot be used in duplicate
Measures :- Change the output No or change the dedicated output parameter

Below are some Notes I made about the RV-2AJ Robot, they may be of help to you