Heidenhain 'Relay ext.DC Voltage Missing' error

Post by bradders » Mon 05 Mar , 2007 16:18 pm

My Triac Heidenhain is showing a 'Relay ext.DC Voltage Missing' error

User avatar
bradders
CNC Guru
CNC Guru
Posts: 1251
Joined: Mon 13 Feb , 2006 12:35 pm
Location: Brighouse, England
Contact:

Post by bradders » Mon 05 Mar , 2007 16:19 pm

This error message 'Relay ext.DC Voltage Missing' is coming on or cannot be cleared if the Emergency Circuit is open at any position (this can be a limit switch or any emergency switch,please see the machine diagram).
You have to check this circuit (e.g. you can make a shortcut between 'Em.circuit output' and 'Em.circuit input').

User avatar
Denford Admin
Site Admin
Posts: 3635
Joined: Fri 10 Feb , 2006 12:40 pm
Hardware/Software: Go to User Control Panel > Profile
Enter as much information about your CNC hardware and software as you can - it makes it easier for everyone to know what you're talking about then.
Location: Sunny Brighouse
Contact:

Post by Denford Admin » Mon 05 Mar , 2007 22:30 pm

you can make a shortcut between 'Em.circuit output' and 'Em.circuit input'
As I remember the Heidenhains, you could only fool the Emergency stop circuit by wiring a relay to the output, and wiring the contact of that relay back into the e.stop feedback.
I'm sure they used to pulse the output a couple of times, and only accept the machine was ok, if it saw the same pulses fed back in.
It was done this way to test for welded relay contacts.