Z axis makes grinding noise when homing
Posted: Thu 19 Mar , 2009 20:30 pm
by boots
Microrouter Compact
S/N u00413-6
Dec. 2003
VR Milling v2.22
When the Z axis is homed, it moves to the limit switch but makes a loud grinding sound instead of stopping and the only way to stop it is to hit the escape key or open the guard. After this, the machine will not jog correctly. it only moves partially up or down.
Posted: Thu 19 Mar , 2009 20:31 pm
by boots
The Home Switch for the Z axis maybe faulty or the switch is loose from its mount. The contacts are not opening properly and the stepper motor is stalling against a physical stop (the grinding noise).
The home switches are NC (Normally Closed). The machine homes by moving to the switch. When the machine pushes the switch, the contacts “open”, then the machine slowly backs away from the switch until the contacts “close”, now it knows it is at “Home”. When you “Home” the X, Y & Z axis’, you will see the machine move to the switch then slowly back off.
Turn the machine off. Use a vacuum cleaner around the switch then use compressed air to blow the remaining dust and chips out from the switch. You should then manually operate the switch several times quickly, you should hear/feel the contacts click as you operate the switch. You can also check the switch with a volt/ohm meter to make sure the contacts are opening and closing properly, if not a new home switch will be needed.
The Z Offset will have to be re-set after installing the new switch.
Posted: Thu 19 Mar , 2009 20:33 pm
by boots
I think that fixed it. Thanks for the reply.
Posted: Fri 20 Mar , 2009 9:06 am
by bradders